Answer:
W_in = 1.353 KW
Explanation:
Given:
- Initial temperature of the house T_1 = 35°C
- Final temperature of the house T_2 = 20°C
- Time taken to cool the house dt = 38 min = 38×60 = 2280 s
- mass of air in the house m = 800 kg
- Specific heat at constant volume c_v = 0.72 kJ/kgK
- Specific heat at constant pressure c_p = 1.0 kJ/kgK
Find:
- Determine the power drawn by the air conditioner.
Solution:
- We will first compute the rate of heat removal from the room, we will use c_v due to a constant volume process, as follows:
Q_l = m*c_v*dT/dt
- In put values given:
Q_l = 800*0.72*(35-20) / 2280
Q_l = 3.7894 KW
- The relationship between the heat rejection and the COP of an air conditioner is given as:
COP = Q_l / W_in
W_in = Q_l / COP
W_in = 3.7894 / 2.8
W_in = 1.353 KW
- Hence the amount of power required for this process is 1.353 KW